Dewpoint - different values. **solved**
Lespius
Post by Lespius »
I notice that the dewpoint displayed on Raw Sensor Data (5.5°) is not the same displayed on MinMAX Data (6.0°):
The correct value for Temp=11.2° and Hum=68% is 5.5°
This is a problem because templates like Weather34 have the wrong value through their API (6.0°).
You can check Brian's answer: viewtopic.php?f=56&t=14398&start=1140
Do you now what's wrong ?
Alain
Re: Dewpoint - different values
Images of your post is missing. No idea why values should differ and I am a bit skeptical that they really do.
Lespius
Post by Lespius »
Ok, I will try to be more explicit.
On one hand you have this:
"Outdoor 5.9° 90% (dew 4.4°, ...)" --> here dewpoint = 4.4°
http://www.meteo-cugy.ch/template/imgs/Capture32.JPG
On the other hand you have the Outdoor Dewpoint sensor --> here dewpoint = 4.9°
"Outdoor dewpoint 4.9°"
http://www.meteo-cugy.ch/template/imgs/Capture33.JPG
So we have two different values for dewpoint: 4.4° and 4.9°
I have checked, with a temperature of 5.9° and a humidity of 90%, the correct value of the dewpoint is 4.4°
So the value of the sensor is wrong. I must say that I have even seen it higher than temperature, which is physically impossible
The yellow color of "outdoor dewpoint" indicates that this logical sensor is manuall redirected to a certain physical temp sensor. Therefore, I am not suprised that values do not match. Can you please show your mapping page?
Lespius
Post by Lespius »
Hm, strange. Could you please provide me a remote login? Please send URL and PW to "info(at)smartbedded.com"
Might be an old calibration infos somewhere in the settings file. But hard to say without having access.
Lespius
Post by Lespius »
Done.
I will be away for a week. So don't be surprised if I don't react.
Root cause is that there has been a calibration of -0.5°C defined for "th0temp".
On the "Raw Data" tab the dewpoint gets calculated from calibrated "th0temp" sensor, while on "Min/Max" tab the dewpoint is taken based on the original "th0temp". When calibration should also apply to "th0dew" it needs to be defined separately for this sensor. I admit that calibrating a calculated dew point value seperately is not best practice, but as Meteobridge does see all sensor data as unconnected data items it has be that way.
I added a calibration of -0.5°C to "th0dew" as well and data looks fine again.
Lespius
Re: Dewpoint - different values. **solved**
Post by Lespius »
Well done, thank you